Approximately zero campgrounds have the capacity to charge more than one EV. They are sized for intermittent loads, just because it uses a 14-50 does not mean it is intended to support 80% steady draw.

Is that not the point of a 14-50 socket? To say that you can draw 50 amps? If you can't supply 50 amps without tripping a breaker, don't install a 50 amp socket.

  • At the risk of saying something obvious, the socket and the breaker are sized for the peak load, not for average load. A typical home might have 300-400 amps if you total up all the breakers even though the mains are 200A or even 100A.

    Also, a bog standard 14-50 is likely not suited for 80% steady EV usage anyway. They make EV-rated 14-50s now because people keep melting the older ones. And that happens even though the vast majority of chargers won't draw more than 32A on a 14-50 due to the historical popularity of using 40A breakers for a 14-50 receptacle.