Comment by jermaustin1
10 hours ago
That's why they said "depending on country"
In North America we are on 120V, making a standard 15A outlet only 1500W max, and something like 1200W sustained. To use higher wattage appliances, we have to upgrade our outlets to 20A (2000/1600W) or up our voltage to 240V, but that carries a different set of plugs and outlets as well.
Usually the home service is 200+ amps these days which is 24 KW total across all circuits, though you're right that most individual circuits are only 10-15 amp.
48kW across all circuits. The 200 amp rating is at 240V for US electrics.
You’re limited to 24kW per leg if you ran everything only on 120V, but any really large server is going to be running off 240V anyways.
> In North America we are on 120V, making a standard 15A outlet only 1500W max, and something like 1200W sustained.
It's 1800W for short periods and 1500W sustained.
1,800 watt for periods less then 3 hours and 1,440 watts for continuous loads over 3 hours.
Realistically, a 15A breaker won’t trip on a 2,300 watt load for at least a few minutes, and often not until a few hours. A listed breaker is expected to trip in several seconds to 3 minutes for a 3,600 watt continuous load.
Take all those numbers and go up by 33% for a house or apartment with 20A circuits (quite common). Go up by 667% for an oven plug.
As anyone who takes care of rentals during winter knows, a typical circuit can tolerate two 1,500 W space heaters without tripping very much (although this is unsafe and a bad idea).